If you want to control the element (pump) couldn't you make a button on the other workspace and have a script in the background that looks for that button to be pushed and changes the state of the pump control on the other worksheet?

I had been planning to do just that.

 

I just tried it with my boil kettle purge gas valve (BK_Gas), and put a control button "Change_BKgas" on my control box status workspace, then have the script below watching it to reflect the change.

[bloop1]
wait "Change_BKgas" State == true

if "BK_Gas" State == false
"BK_Gas" State = true
else
"BK_Gas" State = false
endif
//sleep 1000
"Change_BKgas" State = false
goto bloop1
This post was modified 5 years ago by natebrews

   
ReplyQuote
(@pbruno3)
Reputable Member Admin
Joined: 7 years ago
Posts: 343
Topic starter  

Good idea. You should have some sleep time in there to keep the cpu from running flat out. 


   
ReplyQuote
(@natebrews)
Active Member
Joined: 5 years ago
Posts: 12
 

Do you need the sleep time in it if you are using a wait statement?  Does it work like a poll or an interrupt (clearly from my perspective it is an interrupt, but inside the guts I'm guessing it is more of a poll thing based on your comment)?  

 

I just checked my system and with that script running the CPU usage is 0.7%.

This post was modified 5 years ago by natebrews

   
ReplyQuote
(@pbruno3)
Reputable Member Admin
Joined: 7 years ago
Posts: 343
Topic starter  

No, you don't need a sleep if there is some buffer time sitting on a wait.


   
ReplyQuote
(@bret-c)
Member
Joined: 3 years ago
Posts: 2
 

Peter,

Sorry to revive an old thread, just watched the full brew day with Brian and bought the Pro version the next day.  I'd love to see an updated version of your scripts now that the one listed here is about 4 years old!

Bret


   
ReplyQuote
(@pbruno3)
Reputable Member Admin
Joined: 7 years ago
Posts: 343
Topic starter  

We actually did not use much of any scripts during the brew day - that was mostly a manual brew. 

That said, the script has not really changed. I’m happy to post the most recent version of my personal rig’s script, but I sincerely encourage anyone looking to automate to build their own from the beginning. Scripts are strongly linked to the Elements of a particular configuration so it can get out of context quickly unless you take the time to fully understand the elements and their hardware. 


   
ReplyQuote
(@pbruno3)
Reputable Member Admin
Joined: 7 years ago
Posts: 343
Topic starter  

Here is the most recent.

[setup]
new value MashVol
new value SpargeVol
new value StrikeTemp
new value MashStep1Temp
new time MashStep1Time
new value MashStep2Temp
new time MashStep2Time
new value MashStep3Temp
new time MashStep3Time
new value PreBoilVolume
new time SteepTime
new value TransferTemp
new string Status

MashVol = 18
SpargeVol = 18
StrikeTemp = 160
MashStep1Temp = 152
MashStep1Time = 01:00:00
MashStep2Temp = 152
MashStep2Time = 00:00:00
MashStep3Temp = 152
MashStep3Time = 00:00:00
PreBoilVolume = 30
SteepTime = 00:00:00
TransferTemp = 65

[prep]
Status = "Ready to Start"
"Step" Type = CountUp
restart "Step"
"Mash Temp" Enabled = true
"Mash Level" Enabled = true
"RIMS Temp" Enabled = true
"Flowmeter 1" Enabled = true
"Valve 1" Enabled = true
"Valve 2" Enabled = true
"Valve 3" Enabled = true
"Valve 4" Enabled = true
"Valve 5" Enabled = true
"Valve 6" Enabled = true
"Valve P1" Enabled = true
"Valve P2" Enabled = false
"RIMS Heat PID" Enabled = false
"RIMS Heat Duty" Enabled = false
"RIMS High Power" Enabled = true
"Pump 1" Enabled = true
"Pump 2" Enabled = true
"RIMS Heat PID" Enabled = false
"Water Input" Enabled = false
"Boil Temp" Enabled = false
"Boil Heat Duty" Enabled = false
"Boil Heat PID" Enabled = false
"Chill Temp" Enabled = false
"Chill Flush" Enabled = false
"Condenser" Enabled = false
"Panel Alarm" Enabled = true
"CONTINUE" State = false
wait "CONTINUE" State == true

[prep_fill]
Status = "Prep Fill"
restart "Step"
restart "Master"
"Valve 1" State = on
"Valve 2" State = off
"Valve 3" State = off
"Valve P1" Value = 60
"RIMS High Power" State = on
"Pump 1" State = off
"Valve 4" State = off
"Valve 5" State = off
"Valve 6" State = off
sleep 5000

[fill]
new value PreMashVol
PreMashVol = MashVol - 4
Status = "Fill"
restart "Step"
"Pump 1" State = on
wait "Mash Level" Value >= PreMashVol
"Valve P1" Value = 35
delete PreMashVol
wait "Mash Level" Value >= MashVol

[prep_strike]
Status = "Prep Strike"
restart "Step"
"Pump 1" State = off
"Valve 1" State = off
"Valve 2" State = on
"Valve P1" Value = 60
sleep 5000
"Pump 1" State = on
sleep 10000
wait "Flowmeter 1" Rate > 5
"RIMS Heat Duty" DutyCycle = 100
"RIMS Heat Duty" Enabled = true

[strike]
Status = "Heat Strike"
restart "Step"
new value PreStrikeTemp
PreStrikeTemp = StrikeTemp - 3
wait "Mash Temp" Value > PreStrikeTemp
"RIMS Heat PID" Target = StrikeTemp + 2
"RIMS Heat PID" Enabled = true
delete PreStrikeTemp

[strike_loop]
if "Mash Temp" Value >= StrikeTemp
	"Brew Alarm" Active = true
	"RIMS Heat PID" Target = StrikeTemp + 1
	goto dough_in
endif
sleep 3000
goto strike_loop

[dough_in]
Status = "Strike Ready"
restart "Step"
"CONTINUE" State = false
wait "CONTINUE" State == true
"Brew Alarm" Active = false
"RIMS Heat PID" Enabled = false
"Pump 1" State = off
sleep 3000
"RIMS High Power" State = off
Status = "Dough In"
"CONTINUE" State = false
wait "CONTINUE" State == true

[mash_prep]
new value MashLevelFull
new value MashLevelLow
new value MashStep
new value MashTempDelta
MashStep = 1
Status = "Mash Step 1"
"AutoMash" State = true
sleep 5000
MashLevelFull = "Mash Level" Value - 2
MashLevelLow = MashLevelFull - 6
restart "Step"
"Valve P1" Value = 40
sleep 5000
"Pump 1" State = on
sleep 10000
"RIMS Heat PID" Target = MashStep1Temp + 2
"RIMS Heat PID" Enabled = true
sleep 30000

[mash_loop]
if "AutoMash" State == true
	if "Mash Level" Value < MashLevelLow
 		if "Valve P1" Value > 30
			"Valve P1" Value -= 1
		endif
	endif
	if "Mash Level" Value > MashLevelFull
 		if "Valve P1" Value < 60
			"Valve P1" Value += 1
		endif
	endif
endif
if MashStep == 1
	if "Step" Value >= MashStep1Time
		Status = "Mash Step 2"
		restart "Step"
		"RIMS Heat PID" Target = MashStep2Temp + 1
		MashStep = 2
	endif
	MashTempDelta = "Mash Temp" Value - MashStep1Temp
endif
if MashStep == 2
	if "Step" Value >= MashStep2Time
		Status = "Mash Step 3"
		restart "Step"
		"RIMS Heat PID" Target = MashStep3Temp + 1
		MashStep = 3
	endif
	MashTempDelta = "Mash Temp" Value - MashStep2Temp
endif
if MashStep == 3
	if "Step" Value >= MashStep3Time
		goto mashout
	endif
	MashTempDelta = "Mash Temp" Value - MashStep3Temp
endif
sleep 5000
goto mash_loop

[mashout]
delete MashLevelFull
delete MashLevelLow
delete MashStep
delete MashTempDelta
Status = "Mashout"
restart "Step"
"RIMS Heat PID" Enabled = false
"Valve P1" Value = 60
sleep 3000
"RIMS High Power" State = on
sleep 3000
"RIMS Heat PID" Target = 172
"RIMS Heat PID" Enabled = true
wait "Mash Temp" Value > 168

[prep_sparge]
new value MinFlowRate
new value MaxFlowRate
new value MashTopLevel
new value MashBottomLevel
Status = "Prep Sparge"
restart "Step"
"RIMS Heat PID" Enabled = false
sleep 5000
"Pump 1" State = off
sleep 10000
MinFlowRate = 0.9
MaxFlowRate = 1.2
MashTopLevel = "Mash Level" Value + 1
MashBottomLevel = "Mash Level" Value - 1
"Valve P1" Value = 35
"Valve P2" Value = 30
"Valve 2" State = off
"Valve 3" State = on
"Valve 1" State = on
"Valve 4" State = off
"Valve 5" State = off
"Valve 6" State = on
"Pump 2" State = off
"Boil Temp" Enabled = true
"Flowmeter 1" Enabled = false
"Boil Level" Enabled = true
"Valve P2" Enabled = true
sleep 5000
"Flowmeter 1" Enabled = true

[sparge]
Status = "Sparge"
restart "Step"
new value SpargeLoop
new bool FlowOK
new bool RIMSOff
SpargeLoop = 0
RIMSOff = false
"Pump 1" State = on
"Pump 2" State = on
sleep 5000
"RIMS Heat Duty" DutyCycle = 55
"RIMS Heat Duty" Enabled = true

[sparge_loop]
if "RIMS Temp" Value > 185
	"RIMS Heat Duty" Enabled = false
	RIMSOff = true
else
	if RIMSOff == true
		"RIMS Heat Duty" Enabled = true
		RIMSOff = false
	endif
endif
if "Flowmeter 1" Value >= SpargeVol
	goto drain
endif
if "Mash Level" Value > MashTopLevel
	"Valve P2" Value += 1
endif
if "Mash Level" Value < MashBottomLevel
	"Valve P2" Value -= 1
endif
if SpargeLoop >= 10
	FlowOK = true
	if "Flowmeter 1" Rate > MaxFlowRate
		"Valve P1" Value -= 1
		FlowOK = false
	endif
	if "Flowmeter 1" Rate < MinFlowRate 
		"Valve P1" Value += 1
		FlowOK = false
	endif
	if FlowOK == true
		if "RIMS Temp" Value > 175
			"RIMS Heat Duty" DutyCycle -= 1
		endif
		if "RIMS Temp" Value < 165
			"RIMS Heat Duty" DutyCycle += 1
		endif
	endif
	SpargeLoop = 0
endif
sleep 1000
SpargeLoop += 1
goto sparge_loop

[drain]
delete MashTopLevel
delete MashBottomLevel
delete SpargeLoop
delete FlowOK
delete RIMSOff
delete MinFlowRate
delete MaxFlowRate
Status = "Drain Mash"
restart "Step"
"RIMS Heat Duty" Enabled = false
"Valve 1" State = off
"Valve P1" Value = 0
"Pump 1" State = off
"Valve P2" Value = 30
sleep 5000
"RIMS High Power" State = off
"CONTINUE" State = false

[drain_loop]
if "CONTINUE" State == true
	"CONTINUE" State = false
	goto boil
endif
if "Boil Level" Value >= PreBoilVolume
	goto boil
endif
sleep 1000
goto drain_loop

[boil]
Status = "Boil Ramp"
restart "Step"
"Pump 2" State = off
"Valve 3" State = off
"Valve 6" State = on
"Boil Heat Duty" DutyCycle = 100
"Boil Heat Duty" Enabled = true
"Mash Temp" Enabled = false
"Mash Level" Enabled = false
"Flowmeter 1" Enabled = false
"RIMS Temp" Enabled = false
"Condenser" Enabled = true
wait "Boil Temp" Value >= 211
"Brew Alarm" Active = true
sleep 3000
"Brew Alarm" Active = false
Status = "Boil"
"Step" Type = CountDown
"Step" Value = 01:00:00
"Condenser" State = on
"Boil Heat Duty" DutyCycle = 75
wait "Boil Temp" Value >= 212
"Boil Heat Duty" DutyCycle = 30
wait "Step" Value <= 00:05:00
"Valve 4" State = on
"Valve 5" State = on
"Valve P2" Value = 100
"Chill Temp" Enabled = true
sleep 5000
"Pump 2" State = on
sleep 10000
"Boil Heat Duty" DutyCycle = 100
sleep 20000
wait "Boil Temp" Value >= 212
"Boil Heat Duty" DutyCycle = 40
wait "Step" Value <= 00:00:00
"Boil Heat Duty" Enabled = false

[chillboil]
Status = "Chill Boil Kettle"
"Step" Type = CountUp
restart "Step"
"Chill Flush" Enabled = true

[chillboil_loop]
"Chill Flush" State = on
sleep 10000
wait "Boil Temp" Value <= 175
"Chill Flush" State = off
sleep 15000
if "Boil Temp" Value > 175
	goto chillboil_loop
endif

[steep]
Status = "Steep"
restart "Step"
"Condenser" State = off
"Boil Heat PID" Target = 170
"Boil Heat PID" MaxOutput = 50
"Boil Heat PID" Enabled = true
sleep 1000

[steep_loop]
if "Step" Value >= SteepTime
	goto whirlpool
endif
sleep 30000
"Pump 2" State = on
sleep 5000
"Pump 2" State = off
goto steep_loop

[whirlpool]
Status = "Whirlpool Fast"
restart "Step"
"Valve P2" Value = 65
"Valve 5" State = off
"Pump 2" State = on
wait "Step" Value >= 00:10:00
Status = "Whirlpool Slow"
"Valve P2" Value = 100
"Valve 5" State = on
wait "Step" Value >= 00:15:00

[transfer_prep]
new value TransferTempLow
new value TransferTempHigh
Status = "Transfer Ready"
restart "Step"
"Brew Alarm" Active = true
"CONTINUE" State = false
wait "CONTINUE" State == true

[transfer]
Status = "Transferring"
"Brew Alarm" Active = false
"Boil Heat PID" Enabled = false
"Chill Flush" State = on
"Valve P2" Value = 30
sleep 3000
"Valve 6" State = off
"CONTINUE" State = false
sleep 30000

[transfer_loop]
TransferTempLow = TransferTemp - 2
TransferTempHigh = TransferTemp + 2
if "Chill Temp" Value < TransferTempLow
	"Valve P2" Value += 1
endif
if "Chill Temp" Value > TransferTempHigh
	"Valve P2" Value -= 1
endif
if "Valve P2" Value > 45
	"Valve P2" Value = 45
endif
if "Valve P2" Value < 25
	"Valve P2" Value = 25
endif
if "Boil Level" Value < 4
	goto pre_shutdown
endif
if "CONTINUE" State == true
	"CONTINUE" State = false
	goto shutdown
endif
sleep 15000
goto transfer_loop

[pre_shutdown]
"Valve P2" Value = 0
Status = "Open P2 for Remainder"
"Brew Alarm" Active = true
"CONTINUE" State = false
wait "CONTINUE" State == true

[shutdown]
start "Brew Reset"
stop "Brew"

   
ReplyQuote
(@bret-c)
Member
Joined: 3 years ago
Posts: 2
 
Posted by: @pbruno3

We actually did not use much of any scripts during the brew day - that was mostly a manual brew. 

That said, the script has not really changed. I’m happy to post the most recent version of my personal rig’s script, but I sincerely encourage anyone looking to automate to build their own from the beginning. Scripts are strongly linked to the Elements of a particular configuration so it can get out of context quickly unless you take the time to fully understand the elements and their hardware. 

Yeah, sorry, I should have been more clear.  I'm actually writing it from a blank slate...  I've read through the docs twice even, but sometimes I like to look at how other people wrote code to go "Ahh, that's a more clever way to accomplish that!"  I appreciate you posting this!


   
pbruno3 reacted
ReplyQuote
Page 3 / 3
Share: